On our plant site we have a Pressure Control valve installed on LP steam line to the drier. The valve has a history of stucking, later a strainer was added before valve to avoid foreign particles. But this time we faced a new issue that for a few minutes (6 mins) pressure abruptly dropped by 2 barg and flow rate dropped by 10 Tn/hr and against this action the valve should been opened to maintain the Pressure but the valve closed (a stopper of 50% is installed which retained 50% opening). The vale is fail-to-close so in case of loss of signal or instrument air failure the valve the valve should have been opened. But in field it was observed that the valve opening dropped from 75% to 50% opening. So, we can't conclude the reason behind this valve behavior. Now the valve is normal but suspected till we overhaul it during any SSD.
Additionally:
There is one PT installed on upstream of valve and one FT installed on downstream of the PCV.
There are three IV's in the LP steam circuit line but none of it was throttled during the running operation.
I have attached the response graph please review.
Is there any possible solution/checks from instrumentation side that we can carry out to rectify this issue?
Additionally: