In one of the gas filtering and metering stations, a butterfly valve (B.V) skid (two runs) is installed upstream ultrasonic-based (USM) metering skid (two streams) such that the outlet isolation ball valve of the B.V skid goes to the same header to which the inlet isolation ball valve of the USM is connected.
The B.V is equipped with smart Siemens positioner and Biffi pilot.
The B.V is required to function as flow limiting tool.
The station PLC (installed in the control room) compares flow rate set values (manually daily-entered) with USM actual flow measurements and sends electrical analog (4/20 mA error signal) to the smart positioner which drives the Biffi pilot and finally this pilot control the B.V movement (opening percentage).
The problem is as follows:
As long as the PLC 'sees' the actual flow (measured by USM) is greater than the flow rate values set points, it forces the B.V to close till reaches 15% opening. Then every thing went into chaos/disorder.
At increasing load demand from power plant, the butterfly valve is strongly throttling the flow, the buffer size between the gas station and the power plant is small (few meters pipeline), the pressure downstream the B.V starts to decay and the DP across the B.V starts to increase, noise / vibration generated in the P/L and the USM paths starts to be lost and of course the error signal of the PLC sent to the B.V is erratic and the USM could give erroneous reading of flow rates 3 times higher than the station max. flow. This situation will continue till we isolate the Butterfly operation.
My Question is :
What is exactly the cause of this problem ?
What is this butterfly doing ?
Could any one give me problem analysis ?
Any suggestions to fix the problem?
The B.V is equipped with smart Siemens positioner and Biffi pilot.
The B.V is required to function as flow limiting tool.
The station PLC (installed in the control room) compares flow rate set values (manually daily-entered) with USM actual flow measurements and sends electrical analog (4/20 mA error signal) to the smart positioner which drives the Biffi pilot and finally this pilot control the B.V movement (opening percentage).
The problem is as follows:
As long as the PLC 'sees' the actual flow (measured by USM) is greater than the flow rate values set points, it forces the B.V to close till reaches 15% opening. Then every thing went into chaos/disorder.
At increasing load demand from power plant, the butterfly valve is strongly throttling the flow, the buffer size between the gas station and the power plant is small (few meters pipeline), the pressure downstream the B.V starts to decay and the DP across the B.V starts to increase, noise / vibration generated in the P/L and the USM paths starts to be lost and of course the error signal of the PLC sent to the B.V is erratic and the USM could give erroneous reading of flow rates 3 times higher than the station max. flow. This situation will continue till we isolate the Butterfly operation.
My Question is :
What is exactly the cause of this problem ?
What is this butterfly doing ?
Could any one give me problem analysis ?
Any suggestions to fix the problem?