1. Is it possible to connect 200 series I/O to Quantum PLC ?
2. Is it possible to connect J810 with 800 series I/O to Quantum PLC ?

Regards,
Robert Mehlman
 
> 1. Is it possible to connect 200 series I/O to Quantum PLC ? <

Yes. You will have to purchase J290 kits for your P453s and J291 kits for your P451s. This gets the 200i/o on S908 remote i/o.

> 2. Is it possible to connect J810 with 800 series I/O to Quantum PLC ? <

If i'm not mistaken the J810 is a S901 drop adapter. If this is true, you will have to replace this with a ASP890300 (gets it on S908). You will also have to replace the rack to a AS-H8xx-209 primary. Hope this helps.

Tim Wehri
Crescent Electric
419.788.9618
 
1. i doubt, could test it...

2. for sure, we have alot of it (program sw concept/unity/proworx)

-Arne
 