Re: Intouch S7 IOServer

A

Thread Starter

Alex Wilson

Is it possible, using the InTouch S7 IOServer to talk to Ethernet (MAC addressed) S7 PLCs and TCP/IP (IP addressed) S7 PLCs at the same time? I am using a Siemens CP1613 card and S7-1613 Industrial Ethernet software, the Com L S7 software will only let me set Ethernet or TCP/IP but not both when setting up a .ldb file. I have read about using NetPro to create an .xdb file that would allow Ethernet and TCP/IP comms links but will the S7 IOServer read a .xdb file?

Alex Wilson
Systems Engineer
Dickinson Integrated Solutions Ltd
Tel: +44 (0)1962 840333
Fax: +44 (0)1962 842011
E-Mail: mailto:[email protected]
Web: www.dickinsoncontrol.co.uk
 
P
Yes it is possible. Com L will let you set up both. Simply separate the two files by a semicolon.

Ronald Powers
SR Product Specialist-HMI
Validation Center
Siemens Energy & Automation
5300 Triangle Pkwy
Norcross, GA 30092
 