Recalibrate RTD Temperature Transmitter

J

Thread Starter

Josh

Dear All,

Please anyone can advise to change calibrated range from -100 to 800 dec to 0 100 deg C, using Hart communicator?

Thanks and regards
Josh
 
G

Gagandeep Singh

First your Transmitter should support HART

If that is so, then you just need to change your calibration range. There are two parameters URV (upper range value) and LRV (lower range value). Change your URV to 100 and LRV to 0. Your transmitter is calibrated.

Before doing this do check the minimum span supported by the transmitter, otherwise you may end up with wrong indications.
 