We have GE Mark V Frame6 DLN2 (Duel fuel) GT.
I have few questions.
1) While in premix steady state purging of primary fuel nozzles is fulfilled by CPD air (say 12bar approx). whereas Liquid fuel nozzle, Atomizing nozzle & Water injection nozzles are cooled by Purge air compressor discharge air (say 15 bar).
My question is why GE not preferred CPD air to purge Liquid fuel nozzle, Atomizing nozzle & Water injection nozzles like primary fuel nozzles?
I think we were spending unnecessarily money on auxiliary power consumption by running purge air compressor (110KW).
2) IBH used to avoid icing formation at IGV blades due to minimum opening of IGV during starting in cold climatic countries. In that case, my question is at 95% of nominal speed (14HS)only IBH will come into service meantime 0-95% of speed how Icing formation at IGV blades neglected.
3) At that time electrical drives changeover all stand by fans/pump will start first then the already running one will stop finally. But while doing TK fan changeover things will not happening like that ie., running fan stops first after sometime lag fan gets start command, what is the reason behind that?
Thanks & Regards
Johnplayers
I have few questions.
1) While in premix steady state purging of primary fuel nozzles is fulfilled by CPD air (say 12bar approx). whereas Liquid fuel nozzle, Atomizing nozzle & Water injection nozzles are cooled by Purge air compressor discharge air (say 15 bar).
My question is why GE not preferred CPD air to purge Liquid fuel nozzle, Atomizing nozzle & Water injection nozzles like primary fuel nozzles?
I think we were spending unnecessarily money on auxiliary power consumption by running purge air compressor (110KW).
2) IBH used to avoid icing formation at IGV blades due to minimum opening of IGV during starting in cold climatic countries. In that case, my question is at 95% of nominal speed (14HS)only IBH will come into service meantime 0-95% of speed how Icing formation at IGV blades neglected.
3) At that time electrical drives changeover all stand by fans/pump will start first then the already running one will stop finally. But while doing TK fan changeover things will not happening like that ie., running fan stops first after sometime lag fan gets start command, what is the reason behind that?