Replacing a 25 Amp Single Pole Contactor

R

Thread Starter

reteagle

Can I replace a 25 amp single pole contactor on my heat pump with a 30 amp single pole contactor? Basically the same except for amp rating.
 
S
> Can I replace a 25 amp single pole contactor on my heat
> pump with a 30 amp single pole contactor? Basically the same
> except for amp rating.

Yes -- with caveats, more is better.

Caveats:

(1) Coil voltage (control) must match exactly -- probably 24VAC on HVAC stuff.

(2) Max voltage rating of contacts should be at least as high as power you're switching, and preferably at least as high as the rating of the unit you're replacing.
 
W
I would add that your heat pump is a motor load so your contactor must also be rated for a motor load.

William (Bill) L. Mostia, Jr. PE
ISA Fellow, SIS-TECH Fellow,
FS Eng. (TUV Rheinland)
SIS-TECH Solutions, LP

"No trees were killed to send this message, but a large number of electrons were terribly inconvenienced." Neil deGrasse Tyson

Any information is provided on a Caveat Emptor basis.
 