RIO Network

L

Thread Starter

Lyn Araujo

I have 140 CRP 931 00 and 140 CRA 932 00 for a network RIO and I wanted to know if they are compatible, 140 CRP 931 this one in the principal rack and 140 CRA 932 00 would be on the only station of the network

These modules are for a PLC Quantum

Is this possible? Will some fault be generated?

I am grateful for the help that they could offer to me
 
R

Robert Willis

The 140CRx93200 are dual cable S908 Remote I/O Adapter and the 140CRx93200 are single cable. It is possible to mix the 140CRx93200 and 140CRx93100 in the same system but all of the 140CRx93200 will have a communication fault on the channel that is not connected.

If you plan to do this I would suggest that you only use channel A of each module. There is no way to turn off the Channel B error light
 