RS Linx Lite and Serial DB9

S

Thread Starter

Stephen Bennett

Greetings List: Can RS Linx Lite communicate via 9 pin serial / Win9X PC to AB PLC 5 / X Processors? Or do I require have a 485 Converter, or a higher platform converter? Thanks: Stephen Bennett Kawasaki Robotics (USA), Inc.
 
B
It depends on the particular PLC5, but most of the modern ones have a 25 pin RS-232 port which is also called a DF1 port. The enhanced models such as the 5/11, 5/20, 5/40, 5/60, and 5/80 have this. The 5/15, 5/25... only use Data Highway to program, which requires an expensive converter. Bill Sturm
 
J

Juan De los Santos Naumov

Yes it is possible. Just use the traditional cross connect cable and let the RSlinx find the right configuration. The default for the PLC-5 is 1200 bps, NP, 1stop bit, bcc.
 
K
Yes Rslinx lite will work. Just choose the rs232-df1 driver in Rslinx. Select the appropriate com port, and the DEVICE as PLC-CH0. Leave the rest and use the Auto-Configure button to verify that your cable connection is valid. Typically the baud rate to CH0 , unless it was altered already, is either 2400 or 1200 baud. Regards Kevin Culp Systek Automated Controls Windsor Ontario
 