I'm trying to program the S7-200 PLC with S7 Micro/win. But I got in trouble in programming as follows: I can't detect the edge up and edge down-positive and negative transition, which is presented by its related function. And this makes my program not continue.

Does anybody face similar experience on this case?
Thanks.
 
D
If you would like to send a copy of you program I would be glad to look at it.

Thank you,

David Adams
Application Engineer
CONTROL PRODUCTS
[email protected]
334-567-2017 office
334-567-8614 fax
334-303-9499 cell
 
M

marc sinclair

Hi,

I think the first think to understand is that this is a reasonably mature piece of kit, so the problem is unlikely to be with the PLC.

Try clearing the PLC and only adding one network - try an input through an edge up (P transition) to SET an output

%I0.0-----------[P]----------[ S %Q0.0 ]

Now make the input HIGH for a short while, and the Output will be latched ON

Right, why doesn't it work in your program?

Marc Sinclair