Scaling Control Values

Nag,

Scaling is when you change the control system input signal to equal the signal seen by the field transmitter. For example, you have a transmitter in the field measuring flow from 0 - 3,000 gpm. The transmitter sends a signal of 4mA at 0 flow and 20 mA at 3,000 gpm (12mA at 1,500 gpm).

All the control system sees is a signal that varies from 4 - 20 mA so you need to "Scale" the signal back again. How it's done depends on the control system, but for example in a crude system you would subtract 4mA to give a span of 16mA then multiply the remainder by 3000/16 (Example: 12ma - 4 = 8, 8 x 3,000/16 = 1,500)

Usually this task is done by the control system. When you assign the inputs to the field devices, a form will ask what 4mA is equivalent to and what 20 mA is equal to and that's it. 4 - 20mA is often referred to as 0 - 100%.

In the control system you might see something other than 4-20mA, for example an early Modicon would convert the 4-20 signal with a 12 bit A-D converter into a count range of 0 - 4095 counts, but the idea is the same.

Roy
 