sensors on devicenet

J

Thread Starter

Joe Nucciarone

hello,

I wish to set up a network of sensors (proximity) and bar code readers across my plant using devicenet or other. I also need to interface this network with an existing modbus network. Can someone point me in the right direction. Are there sensors that i could plug directly to modbus? Bar code readers have an rs232 o/p, how do i convert it to devicenet or modbus?

Thanks for your time
 
T
hello, Try calling WAGO I/O support (262-255-6222). WAGO offers a Programmable Dnet Bus communication module like a PLC. A RS232/485 module can be added to the node to talk Modbus. With Wagos IEC-1131 programming tool a program can be download in the Dnet Comm module that creates a Modbus protocol through the RS232/485 module and brings the data back so the Modbus data can be sent to the Dnet Master.
 
M

Maxym Tyutyunnyk

If the bar code readers have the simple interface, it is possible to try realize by XMIT command
Converter RS 232/485 is necessary only if the controller has no RS232

Regards
 