Siemens PC 677B panel

L

Thread Starter

Luiz Rodriguez

How do you set the PC 677B key panel to transfer mode. I require to transfer the project to the PC 677 station, but cannot access the transfer mode function or HMI settings.
 
Hello,

I am not sure about that, but PC 677 is a standard PC, not a panel. Transfer mod is only by Siemens Panels with WinCC flexible integrated like MP377 for instance.
 
L

Luiz Rodriguez

I have found the problem. The Siemens PC677B panel requires WinCC runtime to be loaded in the panel. You then have to purchase a runtime license package with the required amount of tags (128, 500 etc).
 