I have an application requirement which demands that a Shutdown valve has to be actuated and the valve opening status has to be indicated in the Control room. The Control room is at a distance of 2 Km from the Shutdown valve. Can you provide a solution?
Following options were studied:
1. Energise a 24 VDC coil relay placed in a Junction Box 1000 metres away from the Control room. Finally energise the 24 VDC Solenoid vlave on the Shutdown valve at a distance of 1000 metres from the junction box through the 24 VDC potential free contact of the Relay. However, there is a chance of drop in the voltage causing unreliable operation.
2. Send a Analog current (4-20 mA) output corresponding to the ON-commnad from the DCS to the Local Control room DCS which is 1700 metres away. From Local Control room DCS, convert the Analog input to a corresponding Digital Output and energise the Solenoid valve of the Shutdown valve at a distance of 300 metres.
Does anyone have a better option?
Following options were studied:
1. Energise a 24 VDC coil relay placed in a Junction Box 1000 metres away from the Control room. Finally energise the 24 VDC Solenoid vlave on the Shutdown valve at a distance of 1000 metres from the junction box through the 24 VDC potential free contact of the Relay. However, there is a chance of drop in the voltage causing unreliable operation.
2. Send a Analog current (4-20 mA) output corresponding to the ON-commnad from the DCS to the Local Control room DCS which is 1700 metres away. From Local Control room DCS, convert the Analog input to a corresponding Digital Output and energise the Solenoid valve of the Shutdown valve at a distance of 300 metres.