Simple question on Modbus RTU

N

Thread Starter

Nilupul

Hi!

I am using MODBUS RTU. I have several slave devices and one master device. I don't know how they should be connected together. Are they need a switch (like ethernet switch) or can we connect them together with any other way.

Thanks in advance.
 
Modbus RTU with multiple slaves works over RS-485.

RS-485 is designed to be parallel daisy chained, from A to A to A, B to B to B, sig gnd to sig gnd to sig gnd, device 1 to device 2 to device 3, etc.

There are RS-485 hubs that are 'active' devices which allow multiple devices to be wired to one common hub, but the hub replicates the 1-to-2-to-3 sequence internally,but avoids the problems inherent when long 'stub' wiring is used to connect a hub and spoke topology.

http://www.cc-concepts.com/products/rs485/hub/
 
I need to know they should connect physically. What are the parts I have to buy? I heard that I need to buy passive taps and line termination units. Can you please help me on that.
 
J

Jerry Miille

Kudos Dave!

You included the sig gnd connection in your description!

There are lots of installations that are "missing" this very important connection.

Jerry Miille