I have some trouble with OPC Server LC 700 v8, connected in Ethernet mode to redundant LC700 D3-R System.

I'm using two OPC Client connected with this server at the same time, the first Client request about 200 Boolean and 100 Real Tag,
the second one about 150 Boolean and 50 Real Tag.

The Server Scan Time is very slow about 10 second when both clients are connected, this time is reduced to 5 second when only one client is connected.

I have already try to reduce the Scan Time over the TagList v8 software but without any result.

How is possible to reduce the Scan Time or improve Server performance?

Best regards
 
A
This problem was solved by increasing from 4ms to 40ms the Duty Off time on the CPU comm parameters.

A.Borgogni
 