I happened upon this site with a web ferret. I saw this description: Solid state relays - control input 4-20 milliamps. This is just what I am looking for, but now can't find any reference to the same. Can anybody help. Many Thanks Colin Cooke
Hi Colin, The thread, "Solid state relays with 4-20 milliamps control input signal", is at the following link: http://www.control.com/control_com/985067784/index_html#985068169 I found it by using the Search box in the lefthand column. Hope this helps, Jennifer Powell
If you want a 4-20ma input, you're probably looking for analog power control, for a larger AC power load, I will assume. I have used Crydom PCV series relays with good results. These relays look just like a standard on/off hockey puck type SSR, but they accept a 2-10VDC input signal and phase switch a substantial AC load (I use one for 20A at 240VAC). If you wire your 4-20 signal to the input with a 500ohm resistor shunted across the input terminals, this will translate into a 2-10VDC signal at the relay input. You can review the specs at: http://www.crydom.com/assets/amod/pcv.pdf Steve Myres, PE [email protected]