First of all thanks for your helpMIKEVI,
Taki27 is most likely Takieddine27 who joined Dec. 23, 2020, looking for a procedure for calibrating SRV GCV for Mark V-equipped units. That user profile lists his profession as 'Service Engineer.'
I had written a very long response trying to explain "calibration" but it's all been said before. And people just don't want to believe it. (I am, after all, the ONLY person saying one CANNOT calibrate an SRV or a GCV or the IGVs--one can only calibrate LVDT feedback. But the myth and wives' tale have many lives and just will not die.)
Takieddine27 did seem to find something useful back then; then asked about downloading. Never got any replies of clarification or appreciation to the responses.
Interesting questions from a service engineer.
Taki27,I tried the first one after a while i start to get diagnostic alarms for TCQA vote disagree
After reading about this if you don't want to reboot you have to approach the calibration values ( zero and 100% stroke ) maximum the values already stored in the EEPROM and that's will take like forever.