steam turbine control valve

STG Governor Control Valve CV#2 suddenly closed to 0% during normal operation and load at 90%. During CV-2 closed CV-3 has started increasing from 20% to 60% and CV-4 increasing from 0 to 20%


During the CV#2 valve repair
  1. Is it possible to keep the unit running with three governing control Valve till next opportunity shutdown? What are risks if any?
  2. Is there any disturb will lead to unit during CV-2 normalize and come in-service? What are precautions taken too avoid unit disturbing
  3. If possible then please clarify & explain in detail, how can we achieve that.
 
STG Governor Control Valve CV#2 suddenly closed to 0% during normal operation and load at 90%. During CV-2 closed CV-3 has started increasing from 20% to 60% and CV-4 increasing from 0 to 20%


During the CV#2 valve repair
  1. Is it possible to keep the unit running with three governing control Valve till next opportunity shutdown? What are risks if any?
  2. Is there any disturb will lead to unit during CV-2 normalize and come in-service? What are precautions taken too avoid unit disturbing
  3. If possible then please clarify & explain in detail, how can we achieve that.
The thing is WHY CV2 "suddenly closed to 0%"....

Any process/diagnostics alarms occured during this event
Can you provide a Schematic/drawing on the mentionned STG

What kind of STG type is installed ...back pressure /condensing any LP steam/process bleed/exctration

We need to know more on this Unit to advise you ...


James
 
Hi

That s a good thing to come and post issue/case here but it is a good thing also to reply at least on our comments /posts...

Dont leave us without update!

Cheers
James
 
The thing is WHY CV2 "suddenly closed to 0%"....

Any process/diagnostics alarms occured during this event
Can you provide a Schematic/drawing on the mentionned STG

What kind of STG type is installed ...back pressure /condensing any LP steam/process bleed/exctration

We need to know more on this Unit to advise you
 
No alarm. This was happened during normal operation.
there is steam extraction for other processing
It is condensing steam
Okay thanks for these inputs..
Can we know controls sytems that is installed ..
Did you try to troubleshoot by using Controlssystems tools /trends..it will be good to have a view on what is goin on by taking some trends and see if at least logic/application code is ok..
 