Tags required for WinCC

J

Thread Starter

jignesh patel

I am using S7-400 H range of Hotstand by PLC With WinCC as Operator station SCADA package.
Is the number of Tags required for a Hotstandby configuration gets doubled than the actual.
If not than what is the configuration required for Hotstandby PLC configuration at operator station level system ie WinCC.
 
Z
The Number of Tags required for S7-400H systems for a WinCC project is the same as an S7-400 system. It is not doubled. A software package REDCONNECT is used for switching CPUs
 