R
We have three 620-35 redundant PLCs (Nodes 15-16, 17-18 & 19-20) on UCN along with one redundant pair of HPMM (Node 9-10)...
"Node 16" is continuously displaying a "Nosynch" message... We carried out the following checks:
1) Synchronised Node 16 (Redundant) with Node 15 (Primary) by turning the "Key to Program Mode"... (No improvement)
2) No visible fault or status LED seen in the PLC Rack...
3) Program reloaded in the LMM from HM... (No improvement)
4) Checked Node 16's LMM by plugging it in a working node (Node 19)... It was found that this LMM was very noisy... Cable noises began increasing at a rate of thousands of counts per sec finally leading to the failure of Node 19 from UCN.... Hence replaced Logic Manager Module (LMM) of Node 16 with a working module... (No improvement)
5) Restarted the entire PLC rack of Node 16... (No improvement)
Please suggest what further checks can be done and what can be done to restore the status of "Node 16"....
Will the changeover take place from Node 15 to Node 16, should some problem occur with Node 15....????
au revoir
Rahul
"Node 16" is continuously displaying a "Nosynch" message... We carried out the following checks:
1) Synchronised Node 16 (Redundant) with Node 15 (Primary) by turning the "Key to Program Mode"... (No improvement)
2) No visible fault or status LED seen in the PLC Rack...
3) Program reloaded in the LMM from HM... (No improvement)
4) Checked Node 16's LMM by plugging it in a working node (Node 19)... It was found that this LMM was very noisy... Cable noises began increasing at a rate of thousands of counts per sec finally leading to the failure of Node 19 from UCN.... Hence replaced Logic Manager Module (LMM) of Node 16 with a working module... (No improvement)
5) Restarted the entire PLC rack of Node 16... (No improvement)
Please suggest what further checks can be done and what can be done to restore the status of "Node 16"....
Will the changeover take place from Node 15 to Node 16, should some problem occur with Node 15....????
au revoir
Rahul