Frame 7 rated at 65MW produces 66MW on base load after a major overhaul on the unit. The turbine buckets were completely changed. The unit produced 70MW on recommissioning. The exhaust temperature TX is 1032 deg F. The temperature reference temp is 1040 deg F. I would like to know why the unit does not try to produce more power, since its present exhaust temp is 1032.