We just had a OSHA-type consultant here. She spotted a 208v 3 phase pigtail connected to a circuit breaker box. The pigtail had a 30 amp labeled receptacle attached and the receptacle was protected by a 30a breaker on each leg. She is claiming that because the receptacle was protected by 3 30a breakers, the plug had to be rated (and marked) 90a.
It is my understanding that the 30a rated receptacle means that each of the three legs is rated at 30a and that each leg protected with a 30a breaker is correct. My opinion is seemingly unimportant as management feels that the OSHA consultant is the fount of all knowledge thus is correct.
I have two questions. (1) Am I correct or is she. (2) Where could I find printed support for my position thru NEMA, National code or anything else.
It is my understanding that the 30a rated receptacle means that each of the three legs is rated at 30a and that each leg protected with a 30a breaker is correct. My opinion is seemingly unimportant as management feels that the OSHA consultant is the fount of all knowledge thus is correct.
I have two questions. (1) Am I correct or is she. (2) Where could I find printed support for my position thru NEMA, National code or anything else.