Tire Changer power connections

D

Thread Starter

dan647

What will happen if the tire changer w/ an AC 230V 3 phase 60 Hz supply be connected to
an AC380-400, 3 phase 50 hz line? The equipment has an option for a 400 VAC, 60 hz connection.

Thank you

 
For the voltage difference you should use a three phase tranformer ie 3X415v primary to 3X220 v secondary. As for 60Hz on 50Hz supply it will make AC induction motors run at slower speed ie 6:5 ratio. If the machine has 400V connection then this should be OK!
NOTE: The tranformer must supply enough current (AMPS) for the total load of the machine.
 
J

Jason Halligan

If the machine is 400V compatable, you need to change the motor conections from Delta to Star.
At 50Hz the machine will run 20% slower than design(not normally a problem with these machines).

Assuming there is no electronic stuff, you will have to check contactor coil voltages, and should be sweet.

Best of luck,

Jason.
 