Trending bug in FactoryLink 7

M

Thread Starter

Marcelo Borges

Hello..

Some time after installing FactoryLink 7, I noticed that trending had stopped working, even though I didn't mess with it and I didn't alter any configuration inside the Starter app. It seems very strange to me since FactoryLink still logs data inside MS-SQL. So, I believe the bug is with the Trending ActiveX.

Can anyone help?

Regards,
Marcelo
 
B
The trending function for the Trend2 graphic found in the "StarterApp' does not work. The requirements for the Auto X-scale parameters are missing.

This "bug" (and others) have been resolved in a Service Pack 1 release. If you are using the Schneider Monitor Pro V7, then contact the local sales/service office.

 