Triconex Tristation Serial Cable
Mark
Does anyone have the Triconex Tristation serial cable pinout? The cable part number is 1600080-0xx.
Thanks,
Mark
Thanks for the response.
It is for the base plate on a Trident. I tried that pin out, a standard null modem cable.
Also tried a few variations. No joy. The latest manual (I have in my paws) actually call out the part number for the cable,
And have this verbiage:
This figure depicts the RS-232 serial cable, which is a standard null-modem cable used to link the serial connector on the MP Baseplate to a PC acting as the Modbus master.
Notice the missing "... or a TriStation PC."
I found an Installation for Trident V2 online;
http://www.infi90.com/Files/Bailey Infi90 Documentation/Triconex/Planning and Installation Guide for Trident v2 Systems.pdf
Pg 253 has the RS-232 Serial Cable pinout.
Pg 41- The MP baseplate serial Protocols are-Slave, RTU mode, optional parity, 1 stop bit. The MP baseplate Ethernet RJ-45 Protocols are- TriStation 1131
It looks like you have to use a RJ-45 Ethernet cross cable as your Trident to Tristation PC connection. The MP baseplate has 3 Tristation ethernet ports.
In my experience, Ethernet is much better than a serial connection for program monitoring and downloads.
good luck
Same verbiage. That cable is for MODBUS.
Other documents recommend using the serial port (on the comm module baseplate) for the first connection to the system. Several reasons.
Sure I agree, IF, you know the IP address. If the system has been configured and the IP address is unknown, the only method to connect is the serial port.
To finish off the thread.
I was able to use the same cable pinout as an Allen Bradley 1747-CP3/1756-CP3 to communicate with serial port three on a Trident CM3021 using the Tristation software.
Good luck,