26-QT High lube oil temp switchs have malfuctioned a couple of time and our TG got tripped through PIM module. 26-QT is directly terminated on TBD of PIM along with other causes also e.g low hydraulic oil pressure etc. Six inputs AND logic (implemented by wires in series on TBD PIM) then give a single contact to <P>. Whenever TG trips we are completely blind that which switch among these 6 actuated.
Therefore initially we decided to install a RTD sensor in place of 26-Qt (which has max. frequency of failure) which will be terminated in <C> and through soft logic a alarm and a contact will be generated through <CD> to PIM TBD. All Other cabeling will remain as it is. Then afterwards we will do the same with other causes of PIM.
Plz let me know wether it is safe to configure a analog trip input on <C> core and getting trip contact through CD core. I have implemented the complete logic, alarms and simulated. Can i configure an RTD in <R> which seem not likely. Is there some other method also.
Best Regards
Therefore initially we decided to install a RTD sensor in place of 26-Qt (which has max. frequency of failure) which will be terminated in <C> and through soft logic a alarm and a contact will be generated through <CD> to PIM TBD. All Other cabeling will remain as it is. Then afterwards we will do the same with other causes of PIM.