A single line diagram would be good to begin hereat power plant when we close incomer feeder that feed customer plant (11kv/480v transformer) the main generator breaker tripped
I have read many topic about it but I need to discuss best solution to solve this out with someone who is familiar with
best regaeds
The most important thing to put in consideration when you have such a problem is both the transformer and generator kVA or MVA,but if you step down 11kV to 480v you mustn't experience inrush currents that will trip protection because your current at the primary side is relatively lower and so inrush should be.at power plant when we close incomer feeder that feed customer plant (11kv/480v transformer) the main generator breaker tripped
I have read many topic about it but I need to discuss best solution to solve this out with someone who is familiar with
best regaeds