Tube and Shell Water Heater Temp control

R

Thread Starter

Ray Pearson

I'm looking at various ways to control the outlet temperature of a tube and shell water heater. There seem to be a few ways to do this and I'm wondering if there is a stardard process control system to do this.

System is as follows:
50# steam is feed to the shell of the heater and water is contained in the tubes within the heater.
As I see it primary temperature control would based on the hot water/condensate level within the heater and a level controller would modulate the condensate discharge valve, but other systems also employ a control valve located on the steam inlet, and this valve is modulated based on the outlet temp as well.

Any suggestions on the process control?
 
B

Bruce Durdle

Better is to use the outlet temperature as primary of a cascade loop. With the steam-side pressure as secondary and controlling the steam inlet valve. The level loop should be stand-alone.
 