V
In a two gen system, two gen which were sharing equal load,one gen is disconnected and then after frequency for both reached 50hz ,gen is resynchronised in the network. so should they share same load as earlier or not?
Consider there are two turbines and two generators (say 1 and 2) in the system with two loads(load 1 and load 2) and the network is interconnected. And for governor and AVR, I am using controllers with set point for speed and voltage. I started up my turbine gen system (for both) and applied loads.
Both the generators are of same capactity and they shared the load equally. Now I disconnected one generator(gen 2) so as expected frequency for first gen drops and then its turbine power increased and first gen took up all the load(load 1 and 2). Meanwhile for gen two, after a sudden rise in frequency (at the moment of disconnecting this generator ), its frequency starts falling by valve closing and turbine power decreases for this gen 2. When both the generators reached 50 Hz frequency (where gen 1 is loaded and gen 2 is not loaded), I resynchronised gen 2 in the network. I observed a little drop in frequency and then turbine power increased a litttle more for both gen and now gen 2 does not share the same load as it shared earlier when both reached 50 hz(i.e. steady state.
Is the behaviour correct??
Consider there are two turbines and two generators (say 1 and 2) in the system with two loads(load 1 and load 2) and the network is interconnected. And for governor and AVR, I am using controllers with set point for speed and voltage. I started up my turbine gen system (for both) and applied loads.
Both the generators are of same capactity and they shared the load equally. Now I disconnected one generator(gen 2) so as expected frequency for first gen drops and then its turbine power increased and first gen took up all the load(load 1 and 2). Meanwhile for gen two, after a sudden rise in frequency (at the moment of disconnecting this generator ), its frequency starts falling by valve closing and turbine power decreases for this gen 2. When both the generators reached 50 Hz frequency (where gen 1 is loaded and gen 2 is not loaded), I resynchronised gen 2 in the network. I observed a little drop in frequency and then turbine power increased a litttle more for both gen and now gen 2 does not share the same load as it shared earlier when both reached 50 hz(i.e. steady state.
Is the behaviour correct??