When turbine is running with normal operation, sudden load throw will taking place during export breaker open and turbine comes to house load and immediately turbine got trip without any alarms in DCS but signal is generated in governor panel what are the possible root causes and how to address the issues......
Events of incident as follows:
@15:47:47 plant is running normal with 6.8 MW (installed capacity 10 MW)
@ 15:47:48 Export breaker open and came to house load 1.0 MW
@ 15:47:49 Turbine trip through governor signal
We checked and found all parameters like control oil pressure / control valve function /turbine speed / vacuum/ frequency found normal but without any DCS alarm turbine got trip.
In first out trip history we found External trip input1....at governor panel
Pl do suggest the specific solution to overcome the issues in future
Events of incident as follows:
@15:47:47 plant is running normal with 6.8 MW (installed capacity 10 MW)
@ 15:47:48 Export breaker open and came to house load 1.0 MW
@ 15:47:49 Turbine trip through governor signal
We checked and found all parameters like control oil pressure / control valve function /turbine speed / vacuum/ frequency found normal but without any DCS alarm turbine got trip.
In first out trip history we found External trip input1....at governor panel
Pl do suggest the specific solution to overcome the issues in future