T
Does anyone knows what is: power PCB and UD90A. because it shows me trip hf84 and it has to do something about this UD90A or power PCB
Please help!!
Best regards
Please help!!
Best regards
I have the same problem bad I have check the power PCB, it works fine.There is a problem with ud90a.Can you tell me what should I replace in ud90 for it to work again.The power PCB is likely the board that interfaces to the IGBT's and current sensors.
The UD90A is the control board.
If you have that fault one of the two are bad. Replace the drive.
From CT's App Notes:
HF84 Current Offset Trim Failure
This trip means there is a problem with the current feedback on the Drive.
On Unidrive Sizes 1 to 4, the trip is probably due to the power PCB in the Drive but a problem with the UD90A control PCB could also cause this trip. On a Unidrive Size 5 the trip is cause by either UD99 PCB or the UD90A PCB. The interconnects between the PCBs could also cause this trip and should be checked.
M | Need help unidrive sp1422 | Motion Control | 0 | |
R | Unidrive M700 with EtherCAT | Motion Control | 1 | |
A | Unidrive UD70-UD70 Communication | Motion Control | 0 | |
M | Unidrive 2402 | Motion Control | 3 | |
H | AC Drive Unidrive SP | Motion Control | 1 |
by Seth Price