Unimat UH404E HMI with Siemens Logo 8

Hello Samir99;
Since your HMI communicates in Modbus, your logo should support this protocol. What is the firmware version of the logo you are using?
I see on the picture that the logo reference ends with 0BA8. With a firmware FS04 or higher you will have the modbus TCP otherwise your logo will not be able to communicate in modbus with your HMI.
Thank you
 