well we faced a unusual trip in frame V machine. we are having Mark VI control system (TMR) and running a frame 5 machine in the refinery. I am giving a SOE of the trip so that experienced members can get a clear view .
1. VCMI diagnoistic alarm from Processor T appeared first " using default input data from T8 (vpro module Z) ". this is recorded all three R/S/T processors
2. VPRO diganotic alarm came for the following
" voting mismatch in the following signals "
a.Speed probe
b.emergency push button
c.cold junction temp
the alarm was going on getting set and reset in the 12 minutes leading to the trip.
3. after 12 minutes the following alarms appeared
" using default input data from R8 (vpro module X)" this is recorded only in R processor diagnostic and " using default input data from S8 (vpro module Y)" this is recorded only in S processor.
4. The machine tripped on speed sensors trouble trip ( happens when the difference in speed between the protection speed sensors used in protection core (77HT1,2,3) and the control
speed sensors (77NH 1,2,3) exceeds more than 5 % .
i analysed the trip and have come to some conclusions
1. the first alarm appeared because real time process value from the vpro z module failed. ( perhaps due to i/o net failure )
2. the second alarm is the next logical sequence , as the system is TMR the voting resulted resulted in the median value selection. as speed probes from x and Y were showing the near same value and from Z was zero , this alarm appeared.
3. this is where the problem starts , the communication from the X and Y also failed , leading to the tripping of the machine. why should this happen.
on analysing the trip log it was seen that the TNH_OS (protection speed signal) had gone zero only for 50ms and then regained its former correct value.
so even though , it is clear what caused the trip , it is not clear why this should happen.
a. why should the communication in all three protection cores fail ?
b. why should the second and third diagnostic alarm indicating communication fail from X and Y be recorded in R and S respectively , but not in all three which is the norm.
c. why should the communication get established itself in the next 50 ms. and now as the machine is running the problem is not occurring.
as all the communication failed, i suspected a common source to the problem and tightened the connections in the TPRO and changed the three io net cables from the vpro to the VCMI. But recently after 48 days after the trip, it happened again. Now i am at loss what to do. the trip is similar in nature. we have restarted the machine and it is running fine now , but the problem remains unclear. Any ideas why this should happen?
1. VCMI diagnoistic alarm from Processor T appeared first " using default input data from T8 (vpro module Z) ". this is recorded all three R/S/T processors
2. VPRO diganotic alarm came for the following
" voting mismatch in the following signals "
a.Speed probe
b.emergency push button
c.cold junction temp
the alarm was going on getting set and reset in the 12 minutes leading to the trip.
3. after 12 minutes the following alarms appeared
" using default input data from R8 (vpro module X)" this is recorded only in R processor diagnostic and " using default input data from S8 (vpro module Y)" this is recorded only in S processor.
4. The machine tripped on speed sensors trouble trip ( happens when the difference in speed between the protection speed sensors used in protection core (77HT1,2,3) and the control
speed sensors (77NH 1,2,3) exceeds more than 5 % .
i analysed the trip and have come to some conclusions
1. the first alarm appeared because real time process value from the vpro z module failed. ( perhaps due to i/o net failure )
2. the second alarm is the next logical sequence , as the system is TMR the voting resulted resulted in the median value selection. as speed probes from x and Y were showing the near same value and from Z was zero , this alarm appeared.
3. this is where the problem starts , the communication from the X and Y also failed , leading to the tripping of the machine. why should this happen.
on analysing the trip log it was seen that the TNH_OS (protection speed signal) had gone zero only for 50ms and then regained its former correct value.
so even though , it is clear what caused the trip , it is not clear why this should happen.
a. why should the communication in all three protection cores fail ?
b. why should the second and third diagnostic alarm indicating communication fail from X and Y be recorded in R and S respectively , but not in all three which is the norm.
c. why should the communication get established itself in the next 50 ms. and now as the machine is running the problem is not occurring.
as all the communication failed, i suspected a common source to the problem and tightened the connections in the TPRO and changed the three io net cables from the vpro to the VCMI. But recently after 48 days after the trip, it happened again. Now i am at loss what to do. the trip is similar in nature. we have restarted the machine and it is running fine now , but the problem remains unclear. Any ideas why this should happen?