Using an Analog Signal/24vDC Binary I/O Cable

C

Thread Starter

clarks

Can i use 18 AWG 600V cable instead of 18AWG 300V cable for PLC panel internal wiring for analog signal (4-20mA) and binary (24VDC), 0.5A signal?

Is there any technical deficiency of utilizing 600V 18AWG cable instead of 300V 18AWG cable?

Please advise
 
S
No, the extra voltage rating in itself won't cause any problems. You might have more trouble finding a cable shielded to your needs and it will take up more volume due to the thicker insulation, but other than that you'll be fine.
 