Dear all,
The field transmitter are power with 24 VDC But at terminals we get 23 vdc and At positive and instrument ground we get 24VDC and at Negative & instrument ground we get 1 VDC. This happens when instrument is connected at field.
Instrument shields are insulated at field as per Emerson installation instruction.
But at test bench, positive & instrument ground is Zero also Negative & instrument ground zero.
So, my question is Why we get voltage in positive & instrument ground at field level????