Alternative solution for HART 275

H

Thread Starter

Hung Lam

Hi everyone,

I would like to survey a cheaper solution in order to configure smart instruments using HART protocol. HART 275 Communicator is good for this purpose but too expensive, US$2500+. I have checked out http://www.hartcomm.org, http://www.thehartbook.com and http://www.romilly.co.uk, but I did not get any available solutions. I prefer the solution with "PDA + HART modem + software" or "Laptop + HART modem + software". The software should configure HART instruments from at least Rosemount, ABB, Yokogawa. The total price of HART modem & software should not exceed US$1200. I am appreciated with any helps. Thanks.

Hung Lam
 
J
<P>We (Smar) make such a handheld based on the Palm platform. The HART interface for the Palm fits models III, V/Vx, m series, I series, and
Tungsten. See:
<a href="http://www.smar.com/products/hpc301.asp">http://www.smar.com/products/hpc301.asp</a>

<P>We also make the laptop interface and software solution. See:
<a href="http://www.smar.com/products/conf401.asp">http://www.smar.com/products/conf401.asp</a><BR>
<a href="http://www.smar.com/products/hi311.asp">http://www.smar.com/products/hi311.asp</a>

<P>My personal preference is the Palm solution because it is very compact and portable.

<P>These two solutions do not access 100% of functionality in all HART devices. However, all universal HART functions and most common practice functions are supported.

<P>The below list shows what HPC301, CONF401 or any HART master should be able to access in any HART slave provided it is supported in the instrument.
<BR>
<PRE>
Parameter R W Class
Circuit Board Serial Number R U
Command Revisions R U
Device Type R U
Manufacturer R U
Number of Preambles R U
Software Revision R U
Hardware Revision R U
Primary Variable R U
Percent of Range R U
Primary Variable Current R U
Quartary Variable R U
Secondary Variable R U
Tertiary Variable R U
Polling Address W U
Unique Identifier R U
Message R W U
Date R W U
Descriptor R W U
Tag R W U
LRL R U
Minimum Span R U
Sensor Serial Number R W U
URL R U
Damping R W U
Fail-safe Mode R U
LRV ("20 mA") R W U
Transfer Function (Square Root) R W U
URV ("4 mA") R W U
Write Protection R U
Final Assembly Number R W U
Slot 0 R C
Slot 1 R C
Slot 2 R C
Slot 3 R C
Set Lower Range Value W C
Set Upper Range Value W C
Loop Test W C
Perform Self-test W C
Reset W C
Input Zero Trim (Calibration) W C
Primary Variable Unit R W C
Current Zero Trim (Calibration) W C
Current Span Trim (Calibration) W C

R Read
W Write
U Universal Command (supported by all HART devices)
C Common Practice Command (supported by most HART devices)
</PRE>

<P>Jonas Berge<BR>
==================<BR>
[email protected]<BR>
www.smar.com
 