<p>We have installed a UDC 2300 for controlling a Single I/P - 2 O/P system. The I/P is a 4-20 ma signal varying for a value between PV 1.00 to 2.00.
<p>Set Point is a value in the range of the I/P value (1.00 to 2.00).
<p>The O/Ps are 4-20 mA signals following the characteistics.
<p>When PV>SP o/p1 should be increased (4 - 20 mA signal in PID Control) while o/p2 should remain 4mA. <br>
When PV<SP o/p2 should be increased (4 - 20 mA signal in PID Control) while o/p1 should remain 4mA.
<p>We lost the initial configuration parameters in a reset. Based on the documentation we have fed in the parameters as follows.
<pre>
UDC2300 Set Up
Timer Timer Disabled
Tuning PB 5.00
Rate T 2.00
I min 3.00
PB 2 9.96
Rate2 T 2.06
I2 min 4.83
Secur 0.00
Lock None
Automatic Enable
A Tune Enable
RnHld Dis
SP-Sel Dis
SP Ramp SP Ramp Dis
SP Rate Dis
Atune Fuzzy Enable
Tune Tune
At Err None
Algor CtrAlg PID A
OutAlg CURD
4-20RG 100.00
Input1 Dec 88.88
Units None
In1typ 20-Apr
XMITR1 Linear
In1Hi 2.00
In1Lo 1.00
Ratio1 1.00
Bias1 0.00
Filtr1 5.00
Brnout Up
Freq 5.00
Lang Engl
Control LSP's One
SPTrk None
Pwr Up Man
SP Hi 2.00
SP Lo 1.00
Action Dir
Out Hi 100.00
Out Lo 0.00
Dband 2.00
FailSF 0.00
FSMode NOL
PB or GN PB
MinRpm Min
Option AuxOut Out
0Pct 2.00
100Pct 1.00
Com Com Dis
Alarms A1S1VA 1.91
A1S1TY Proc
A1S2TY None
A2S1TY None
A1S1HL High
ALHYST 0.10
ALARM1 NO
BLOCK Dis
</pre>
<p>Could anybody who is familiar with this Controller confirm whether the settings are correct for the system or please suggest alternatives.
<p>Best Regards
<p>Parag Bhadra<br>
Metso Minerals<br>
6th Floor DLF Gateway Towers<br>
DLF City Phase III<br>
Gurgaon<br>
Haryana
<p>Set Point is a value in the range of the I/P value (1.00 to 2.00).
<p>The O/Ps are 4-20 mA signals following the characteistics.
<p>When PV>SP o/p1 should be increased (4 - 20 mA signal in PID Control) while o/p2 should remain 4mA. <br>
When PV<SP o/p2 should be increased (4 - 20 mA signal in PID Control) while o/p1 should remain 4mA.
<p>We lost the initial configuration parameters in a reset. Based on the documentation we have fed in the parameters as follows.
<pre>
UDC2300 Set Up
Timer Timer Disabled
Tuning PB 5.00
Rate T 2.00
I min 3.00
PB 2 9.96
Rate2 T 2.06
I2 min 4.83
Secur 0.00
Lock None
Automatic Enable
A Tune Enable
RnHld Dis
SP-Sel Dis
SP Ramp SP Ramp Dis
SP Rate Dis
Atune Fuzzy Enable
Tune Tune
At Err None
Algor CtrAlg PID A
OutAlg CURD
4-20RG 100.00
Input1 Dec 88.88
Units None
In1typ 20-Apr
XMITR1 Linear
In1Hi 2.00
In1Lo 1.00
Ratio1 1.00
Bias1 0.00
Filtr1 5.00
Brnout Up
Freq 5.00
Lang Engl
Control LSP's One
SPTrk None
Pwr Up Man
SP Hi 2.00
SP Lo 1.00
Action Dir
Out Hi 100.00
Out Lo 0.00
Dband 2.00
FailSF 0.00
FSMode NOL
PB or GN PB
MinRpm Min
Option AuxOut Out
0Pct 2.00
100Pct 1.00
Com Com Dis
Alarms A1S1VA 1.91
A1S1TY Proc
A1S2TY None
A2S1TY None
A1S1HL High
ALHYST 0.10
ALARM1 NO
BLOCK Dis
</pre>
<p>Could anybody who is familiar with this Controller confirm whether the settings are correct for the system or please suggest alternatives.
<p>Best Regards