We have a distributed PLC system consisting of 105 PLCs out in the field. There are 14 RS-485 runs and master SCADA is polling each PLC through etehrnet-serial gateways. Communication is Modbus.
6-7 months ago a lightning hit some part of the field and some PLCs stopped communicating. We have surge protectors at the communication line and panel power inlet. The PLCs were all good, there was nothing wrong with the ports, but they were just not communicating. After trying everything I could for a month or so, I isolated the PLC rack from ground and used a DC/DC convertor just to feed the PLC. That could only solve the problem. So I did this for each panel with this problem.
Last month again a lightning hit the field, this time different area. And same thing happenned. I solved the problem the same way.
Any idea how this solution works and what is happenning to my system. Is it possible that the modbus cable may change empedance with the effect of the voltage peak?
6-7 months ago a lightning hit some part of the field and some PLCs stopped communicating. We have surge protectors at the communication line and panel power inlet. The PLCs were all good, there was nothing wrong with the ports, but they were just not communicating. After trying everything I could for a month or so, I isolated the PLC rack from ground and used a DC/DC convertor just to feed the PLC. That could only solve the problem. So I did this for each panel with this problem.