ABB/ACS880 VFD Not Running in Auto
ABB/ACS880 vfd will not run in auto run. Controlling from a micrologix 1200 and analog I/O module.

ABB/ACS880 vfd will not run in auto run. Controlling from a micrologix 1200 and analog I/O module. I can switch the control switch at operator panel to the "jog" position and drive and Motor will run. I can also run motor from drive manually in "Local" position on HMI.

Richie
pensfan66rs@gmail.com

By Steve Myres on 28 January, 2019 - 10:36 am