Sunday, August 25, 2019
Communicating with Device over Modbus RS 485 and TCP/IP
Communicating with Modbus RTU devices via a Modbus TCP/IP gateway
I am working with a TGW-715 Modbus gateway which is connected to a Modbus device.
Modbus device is configured with following parameters:
-baudrate 9600
-rtu
-modbus enable
-adress 1
-parity none
And I also configured the gateway with these parameters.
I connected the D1+ and D1- of the gateway to B and A of the Modbus device.
But when I want to test if everything is working on Modbus Doctor, I got the exception code 0B which means that there was no response from slave.
I tried to increase the timeout to 3000ms but still get no response.
Do you have any idea why?
Change the A and B driver line connections on one end.
The labeling of the lines is not standardized. If connected backwards, it won't damage the drivers but it won't work.