Back Ground:-
I am working on MS5002C. Control is TMR - Mark 6 Dual fuel (Gas and Liquid) - Non DLN
The unit is in Operation since 3 years.
Unit was online since 2 months.
Operations wanted to Test some faulty alarms created by Gas detectors in Filter house and Turbine compartment. They gave a normal shutdown. As soon as it start coasting down, the unit tripped on "Compressor Bleed Valve Pos Trouble Trip" - L33cb1o
and not l33cb2o
We checked the solenoid, we can hear the click sound as we energize, measured 108 VDC while energize - Ok.
Now, when we start unit, tripped around 1800 rpm
- due to same problem - l33cb1o just shows Close for a second and Opens and Unit Trips.
Tried adjusting L33CB1O - did adjustment
Secondly, started again, monitored l33cb1o / L20CB, the unit tripped again at 3500 rpm on l33cb10 - compressor Bleed Valve Position Trouble Trip. [l33cb1o just closes and Opens back again]
(L20CB was still de-energized - never energized in both cases)
(If solenoid was passing, it should effect both bleed Valves, but here only l33cb1o was doing the trouble.)
So, checked continuity on both limit switches L33cb1o /l33cb2o
a) (Switch to marshaling with knives Open = 9.5 oHMS)
b) (Switch to marshaling with Knives in = 78Kilo Ohms)
c) Each wire w.r.t Panel chassis = 1.8 ohms
L33cb1o was showing mega Ohms for knives open [marshaling to Switch], but later replaced terminals at switch which reads the above for both now.
Q1) Do you think is the problem solved now, Or still have to clear the ground on each wire?
Q2) Is there something else to check apart from the ground?
Q3) Can we start the Unit in this state if urgency by Operations?
Would request your advice on the above.
I am working on MS5002C. Control is TMR - Mark 6 Dual fuel (Gas and Liquid) - Non DLN
The unit is in Operation since 3 years.
Unit was online since 2 months.
Operations wanted to Test some faulty alarms created by Gas detectors in Filter house and Turbine compartment. They gave a normal shutdown. As soon as it start coasting down, the unit tripped on "Compressor Bleed Valve Pos Trouble Trip" - L33cb1o
and not l33cb2o
We checked the solenoid, we can hear the click sound as we energize, measured 108 VDC while energize - Ok.
Now, when we start unit, tripped around 1800 rpm
- due to same problem - l33cb1o just shows Close for a second and Opens and Unit Trips.
Tried adjusting L33CB1O - did adjustment
Secondly, started again, monitored l33cb1o / L20CB, the unit tripped again at 3500 rpm on l33cb10 - compressor Bleed Valve Position Trouble Trip. [l33cb1o just closes and Opens back again]
(L20CB was still de-energized - never energized in both cases)
(If solenoid was passing, it should effect both bleed Valves, but here only l33cb1o was doing the trouble.)
So, checked continuity on both limit switches L33cb1o /l33cb2o
a) (Switch to marshaling with knives Open = 9.5 oHMS)
b) (Switch to marshaling with Knives in = 78Kilo Ohms)
c) Each wire w.r.t Panel chassis = 1.8 ohms
L33cb1o was showing mega Ohms for knives open [marshaling to Switch], but later replaced terminals at switch which reads the above for both now.
Q1) Do you think is the problem solved now, Or still have to clear the ground on each wire?
Q2) Is there something else to check apart from the ground?
Q3) Can we start the Unit in this state if urgency by Operations?
Would request your advice on the above.