I have a micro 1100. Need to run both pressure sensors 450 ft. I have 18 gauge/4 shielded Pairs. I did a test with the 1000 ft roll. 7 Ohms total. Voltage (24 Vdc) Dropped only 200 mil amps. Not Bad. Note: I need only 450 ft +/- and NOT THE 1000 FT. The SIGNAL WAS OFF A LITTLE.
Had it set for 0 to 100. Tank Level. I had 10 to 99.
Had it set for 0 to 100. Tank Level. I had 10 to 99.