Can I know if we can /
Liquid to Gas fuel transfer is typically done at lower loads 20-30% load. Maximum load this is done is typically ~100 MW. that would prevent higher load LF to GF transfer.
For Gas to liquid transfer, this is pretty much unrestricted and can be done at any load. However it is a good practice to limit it to maximum load to 80% load to give some margin for IGV regulation and over-temperature protection.
Liquid to Gas fuel transfer is typically done at lower loads 20-30% load. Maximum load this is done is typically ~100 MW. that would prevent higher load LF to GF transfer.
For Gas to liquid transfer, this is pretty much unrestricted and can be done at any load. However it is a good practice to limit it to maximum load to 80% load to give some margin for IGV regulation and over-temperature protection.