The 250 ohm resistor in HART is a shunt resistor just like the terminator for FOUNDATION fieldbus.
The HART communication signal works this way:
The talking device transmits a current
The listening device picks up on voltage
The purpose of the 250 ohm shunt resistor is to convert the transmitted
current to a voltage the received can pick up
Take a look at chapter 11 in the yellow book "Fieldbuses for Process
Control: Engineering, Operation, and Maintenance" buy online: http://www.isa.org/fieldbuses
YES. Unless you wish to apply the 24 volts DC of your loop power supply directly across the Analog Input terminals that expect to see a 1-5 volt drop across this 250 ohm resistor. I don't think so.
If you are not using the 4-20 mA analog signal from a HART instrument, why are you using HART's analog transmission. There is also a faster, though less used, PSK multidrop version of HART that does not need a 250 ohm signal because there is no 4-20 mA signal. Read all about HART at http://hartcomm.org.
Dick Caro
Richard H. Caro, Certified Automation Professional, CEO, CMC Associates,
2 Beth Circle, Acton, MA 01720
Tel: +1.978.635.9449 Mobile: +.978.764.4728
Fax: +1.978.246.1270
E-mail: [email protected]
Sorry Jonas, I do not believe you are correct. In my previous reply to this question, I pointed out that the 250 ohm resistor converts the 4-20 mA analog signal from the HART transmitter to a 1-5 volt drop to allow the Analog Input card of the DCS or PLC to read the analog signal. The HART digital FSK (Frequency Shift Keying) signal is also present on this line and supplies the HART digital data to the HART modem chip usually present on the same Analog Input card for all new DCSs and PLCs. The Bell 202 protocol used for this FSK
digital circuit needs no terminating or load resistor. The 250 ohm resistor is only for the analog circuit.
Dick Caro
You don't.
The HART signal is a high frequency superimposed on the analog signal. In order to receive the signal you need a means of creating a some impedance in the loop, a resistor does this.
If you were to connect the transmitter directly across a 24 VDC power supply, the analog signal would be just fine but the HART signal would be damped right out. If you add some resistance in the loop you will get some DC voltage drop but also across the resistor you will get the HART signal.
There's nothing magic about the value 250, it will work with less e.g. 200. It would also work if instead of a resistor you added a choke.
Do us all a favour - If you have a communicator and power supply try a range of resistors and let us know the minimum value that you can get to work.
The literature says 250 because that's a common value.
Sorry to disagree again with you Roy, but the 250 ohm resistor in the HART circuit is there for the ANALOG signal, not the digital signal. With 20 mA DC in the loop, typically full scale, the voltage drop across the precision 250 ohm resistor is exactly 5 volts. The A/D converter in the Analog Input card expects a range of 1-5 volts to interpret the analog transmission of a HART instrument. The resistor has nothing to do with the LOW Frequency digital signal (1200 bps)
of the HART digital transmission.
Changing the resistor to something else would certainly not effect the digital HART signal, but it would kill the calibration of the analog HART signal.
Dick Caro
shows the 250 ohm resistor adapter plugged directly into the 275 (and in series with the loop), using the pair of banana jacks on 3/4" center with the supplied banana plug adapter across which a ~250 ohm resistor is connected.
When using the 250 ohm resistor in this fashion, the voltage drop across the 250 ohm resistor is placed outside of the receiver device's analog input, if there is one in the loop. The illustration cited shows no receiver device in the loop, only the DC power supply, the HART device and the 275, not untypical of a bench 'cal' for commissioning.
In my experience, the 275 communicator works just as well if the 250 ohms is across a receiver device's AI, but bench testing or field commissioning might not have a complete loop circuit through an AI with its dropping resistance, which is what I think the illustration is trying to show.
Carl, you have it right. The HART instrument expects to operate in a full loop with an analog input board where the termination has a 250 ohm precision resistor to provide the 1-5 volt drop for translating the 4-20 mA current signal to a voltage. If you attempt to operate the 275 without the termination of the AI circuit, you must provide another 250 ohm resistor, as for bench calibration.
If the 274 is connected across the 4-20 mA line of an operating instrument, then the bench test 250 ohm resistor is not needed. The 275 draws its power from the operating 4-20 mA loop so must be placed in series with that loop, but it can do this when the AI board with a 250 ohm resistor is already installed, by connecting across the line. The 275 only needs to detect the digital HART signal.
Dick Caro
I don't disagree with you that the 250 is used for analog in a 1-5 volt input, but not all input modules are 1-5. I have used Modicons where the input was 50 Ohms.
If you are testing a Hart device in the shop you might have a power supply, a multimeter and a HART communicator. You hook the transmitter, the multimeter and power supply in series. Now where do you hook the HART communicator? Obviously you need some loop resistance, All I am saying it doesn't have to be a precision 250 Ohm resistor, any old thing will do, e.g. 147 Ohm, 220 Ohm, 570 Ohm, an RTD, a transformer primary, a light bulb... anything that will give you some loop impedance.
Your statement "The 275 draws its power from the operating 4-20 mA loop" is not quite correct. It has its own internal battery. If you read the original post, Shankar asks, "Why we need to use 250 Ohms While using HART"? From that I assumed he was using HART without analog, that's why I said "You don't."
If you connect a transmitter directly across the power supply, that's an operating instrument and the HART signal will still be there, but you need some form of reactance or resistance so the HART communicator can pick up the change or modulate the current. When you use the communicator in the field the resistance is supplied by the wiring and any input resistance.
I did a project with a Modicon (50 Ohm 0.2-1V) I found the communicator would not work at the panel but worked OK at the transmitter because of the additional wire reactance. I guess what I am trying to get across, there's nothing magic about the number 250, 220 or 570 will work just as well.
there's no magic behind 250 ohm..yeah!..it could give a drop of volts from 1v to 5v, but get this..
the dc power supply we use in the loop has low pass capacitor filters, and in absence of a resistor, the filter is in parallel with the Tx, thereby bypassing the digital information , and adding a resistor just provides an impedance btn the Tx and filter circuit!
and yeah!..you can go up to 1000 ohms too!..
so chill out!!!..yo!!
the HART communicator to function properly a minimum of 250 ohs resistance must be present in the loop. The HART communicator does not measure loop current directly.
HART Communication technology has a very low power requirement typically working on less than 3.8 mA of current. HART utilizes a frequency shift keying (FSK) modem to communicate over the primary variable analog signal wires. By imposing the digital signal on top of the 4-20mA analog loop, HART allows for a simultaneous analog signal with a continuous digital communication signal that has no effect on the analog signal.
HART circuits or networks can be configured in one of three ways, through a conventional connection method (point-to-point), multi-drop (point to multiple points) or through a multiplexer (HART to RS-485). HART Communication is designed so that there must be minimum resistance in the current loop before communication will occur. The HART specification accommodates loop resistances of 230 to 1100 ohms, typically a 250-ohm resistor is recommended.
Power supply impedance is minimal as opposed to current source being infinite.
To wire 24V right across a transmitter and using hart communicator connectors across the transmitter would be the same as connecting them on the same side.
The 250-ohm resistor is not placed in the loop for the idea of converting the current (4-20mA)from transmission to voltage (1-5V)for reception, and also the value 250 is not a special value for a loop resistance needed for HART communication.
Explaining first the true purpose of having a resistor in the loop:
The HART communicator is communicating with the transmitter through FSK protocol. Understanding this protocol, it is a communication in analog platform. Digitalization of the signal happens within the HART devices and not along the transmission line.
The resistor's position in the loop is between the transmitter and the DC power supply. As we connect the communicator it should be tap between the resistor and the transmitter or directly parallel to the resistor. Why? Because the power supply has a LOW PASS CAPACITOR filter that basically squelches analog signals like ripples. Thus, if there is no resistance in between the PS and the TX that analog signal coming from the HART devices will only be filtered out.
Explaining the value 250:
The resistance value is not necessarily be 250 ohms. Maybe because of the idea that the controlling current of 20mA will give us 5 volt calibration if there is a loop resistance of 250 ohms. Maybe not a good theory.
Actually you can use a number of possible resistance values that will allow communication between HART devices. This value depends on the transmitter minimum operating voltage requirement. Simple OHM's LAW. For example, if the voltage requirement for a certain transmitter is 12-24 volts use a resistor that will not give you a drop of below 12 volts or else you will not deliver power to your transmitter. Most transmitters are supplied with 24 volts and as per computation 250 ohms to 500 ohms gives a drop of almost 18 v which is somewhat in between the operating voltage.
But you need some means of developing a voltage drop that the HART communicator can see e.g. a reactor or resistor of high enough value.
Without the resistor the load is too low in impedance and it shunts the signal.
Some seem fixated on 250 Ohms but in reality 100 might be enough and 500 not too much.
-->yes you are right, i like to say another point here that 4-20mA converted into voltage by using 250 ohm Resistor, DCS accept only voltage signal 1-5v
-->if you are sending signal 10-50mA then you should use 100 ohm Resistor to convert into voltage 1-5V
-->if you send the voltage signal 1-5V then no Resistor is needed ,directly given to the DCS according to the Priority wise (+ and -),if the priority is interchanged then in DCS Soft File Error will be coming
Rakesh Kumar.N BE Instrumentation Engineer
Trainee in MFL, Looking for a good job [email protected]