BN Axial Probe adjustments
Sensor technologies. topic
Posted by Hamad on 15 June, 2009 - 1:31 pm
Hi everybody,

on a BFW pump we adjusted the gap voltage on an axial position for -9.75 VDc as per BN spec. but the problem is when the motor starts the shaft will shift momently by 0.4 mm beyond the trip s.p., after few seconds the shaft will go back to normal position.

does anybody knows if there a configuration on BN where this trip can be avoided when starting the motor, maybe by increasing the gap voltage in order to inhibit this trip when starting the motor.

Thanks,
Hamad


Posted by vahid on 16 June, 2009 - 12:51 am
Hamad,

What do you mean by BN? Does it mean Bently Nevada vibration monitoring system?

If it is Bently, what is the model of your system?

Normally there is capability to inhibit the trip/Shutdown signal, even you can set a specified time to pass from critical condition during start up.


Posted by bubba_gump on 16 June, 2009 - 7:00 am
Leave gap alone. If you have a 3500 rack, get the config software from your Bently Service location.

enable the trip multiplier for that channel.

Maybe get a Bently service rep to help you. GE owns them.

What this does is temporally increase your trip setpoint (during a start, for instance).

Good Luck

Your use of this site is subject to the terms and conditions set forth under Legal Notices and the Privacy Policy. Please read those terms and conditions carefully. Subject to the rights expressly reserved to others under Legal Notices, the content of this site and the compilation thereof is © 1999-2010 Nerds in Control, LLC. All rights reserved.

Users of this site are benefiting from open source technologies, including PHP, MySQL and Apache. Be happy.


Fortune
You are only young once, but you can stay immature indefinitely.
Advertise here
Advertisement
our advertisers
Help keep our servers running...
Patronize our advertisers!
Visit our Post Archive