R
We have 1990 vintage GE frame 6's, dual fuel, although since they were installed, no gas fuel supply was piped in to them. Normal fuel is #2 fuel oil.
The present thought is to remove the flexible gas fuel lines, and install blanks at the gas fuel manifold flanges and the gas connection at the duel fuel burners.
The intent is to give more working room in the turbine compartment, since there are no plans to run a gas fuel line to the site in the foreseeable future.
Before the storm troopers get turned loose on this project, my question is:
Although we do not use gas fuel, there is gas fuel purge air going through the manifold, piping and to the combustion cans.
By blanking off this air, will we see continuous black smoke spewing at out next run?
Besides serving as a manifold purge.... is it serving as a "secondary air" or some other important function?
(better to ask the silly question now.... instead of having to undo a "leap before you look thing!)
Thanks!
RTK
The present thought is to remove the flexible gas fuel lines, and install blanks at the gas fuel manifold flanges and the gas connection at the duel fuel burners.
The intent is to give more working room in the turbine compartment, since there are no plans to run a gas fuel line to the site in the foreseeable future.
Before the storm troopers get turned loose on this project, my question is:
Although we do not use gas fuel, there is gas fuel purge air going through the manifold, piping and to the combustion cans.
By blanking off this air, will we see continuous black smoke spewing at out next run?
Besides serving as a manifold purge.... is it serving as a "secondary air" or some other important function?
(better to ask the silly question now.... instead of having to undo a "leap before you look thing!)
Thanks!
RTK