We are facing hunting in 77fd-1, 77fd-2 while the gas turbine (fr 9 -Mk Vie) is running on gas fuel. i.e the signal (fdbk-77fd1,2) has a non zero value and varying up to certain values, approximately 10HZ. this caused alarm of (liquid fuel bypass trouble) and inhibit transferring the fuel to liquid fuel if this value increased above a certain constant (3) for 10 sec.
Some how it's being a cause of tripping of LIQUID FUEL TROUBLE ALARM L3FLT. Below are the mentioned step that we have investigated
we have checked the gap voltages of probe & found normal as per device summary which is 0.26mm.
We also have check the complete loop of the sensor till BCCA card found normal.
We also have check the coil resistance as well which were found quite normal 525 Ohm.
Some how it's being a cause of tripping of LIQUID FUEL TROUBLE ALARM L3FLT. Below are the mentioned step that we have investigated
we have checked the gap voltages of probe & found normal as per device summary which is 0.26mm.
We also have check the complete loop of the sensor till BCCA card found normal.
We also have check the coil resistance as well which were found quite normal 525 Ohm.