Hello
Recently I got Schneider Electric's meter PM710 which I connected to citect server through Modbus to TCP gateway Moxa MB3170.
With program such as CAS Modbus Scanner I have no problem reading registers. For example:
401000 = 0x44C3 401001= 0x03F1
Float value of 0x44C303F1 is 1560.1232 (exact value visible on meter). If I understand correctly I should choose FloatMode = 1 (3210) but unfortunately its not working. I used all FloatMode options (0-3) and none of them give me sensible values.
My configuration:
[PM710]
Firmware 3.110
MODBUS RTU
Address: 19
Baud rate: 9600
Parity: None
Connection: RS-485 (2xwire)
[Citect]
-BOARD-
Board Name: BOARD 1
Board Type: TCPIP
Address: 0
-PORT-
Port Name: PORT72_BOARD1
Board Name: Board 1
Special Opt: =-I***.***.***.*** -P502 -T
-I/O Device-
Name: PM710_19
Address: 19
Protocol: MODNET3
Port Name: PORT72_BOARD1
Cache: TRUE Cache Time: 500
Background poll: TRUE Background Rate: 00:00:20
-citect.ini-
[MODNET.PORT72_BOARD1.PM710_19]
FloatMode = 3
-Equipment-
Tag Name: TAG_{equipment.IODEVICE}_Real_Energy
Data Type: Real
I/O Device {equipment.IODEVICE}
Address: 41000 (I also tried 401000 and 301000)
Cluser Name: {equipment.CLUSTER}
Could You please help me with my problem?
Best Regards
Recently I got Schneider Electric's meter PM710 which I connected to citect server through Modbus to TCP gateway Moxa MB3170.
With program such as CAS Modbus Scanner I have no problem reading registers. For example:
401000 = 0x44C3 401001= 0x03F1
Float value of 0x44C303F1 is 1560.1232 (exact value visible on meter). If I understand correctly I should choose FloatMode = 1 (3210) but unfortunately its not working. I used all FloatMode options (0-3) and none of them give me sensible values.
My configuration:
[PM710]
Firmware 3.110
MODBUS RTU
Address: 19
Baud rate: 9600
Parity: None
Connection: RS-485 (2xwire)
[Citect]
-BOARD-
Board Name: BOARD 1
Board Type: TCPIP
Address: 0
-PORT-
Port Name: PORT72_BOARD1
Board Name: Board 1
Special Opt: =-I***.***.***.*** -P502 -T
-I/O Device-
Name: PM710_19
Address: 19
Protocol: MODNET3
Port Name: PORT72_BOARD1
Cache: TRUE Cache Time: 500
Background poll: TRUE Background Rate: 00:00:20
-citect.ini-
[MODNET.PORT72_BOARD1.PM710_19]
FloatMode = 3
-Equipment-
Tag Name: TAG_{equipment.IODEVICE}_Real_Energy
Data Type: Real
I/O Device {equipment.IODEVICE}
Address: 41000 (I also tried 401000 and 301000)
Cluser Name: {equipment.CLUSTER}
Could You please help me with my problem?
Best Regards