Thursday, May 24, 2018
DORIC Temperature Indicator
DORIC digital temperature indicator used in Mk 2 panel does not indicate any temperature value, but only flickers. It is a mv to temp. converter for "K" type thermocouple.
By sultan Khan on 17 May, 2018 - 11:16 am
The DORIC Model 400A type Digital temperature indicator is used in Mk2 speedtronic panel for "K" type Thermocouple monitoring. When power is applied (115V AC )to it, it indicates "0" deg C. When mv signal is applied to it +v and -V terminal, it does not indicate mv equivalent deg C. It is a new temperature indicator. The DIP switch setting is the same as that of other meter. This meter is for use with the K type Thermocouple.
There is no removable parts by which we can interchange certain chip or display part from one to another.
What could be the other problem? Any one experienced such thing in the meter, can please help me out.
Thanx..
The Doric series 400 manual at this URL:
https://intertechnology.com/Doric/pdfs/400_Series.pdf
shows each model has an 'order code', a 3-xx code, that defines that unit's functionality.
For instance, the K type T/C indicator is 3-01.
The 4-20mA input indicator is 3-61.
Is your device an order code 3-01?
By sultan khan on 18 May, 2018 - 12:53 pm
Mr. David..
Thanks a lot for your kind response. the meter was ordered by some one long back. Meter stamping indicates it is for K type TC. If by chance it is for ma input, then is there any changes is to made in DIP switch setting? to change to mv input. Kindly let me know. I shall also go through the PDF mentioned by you..
Thanks for your response, once again....
By DAMENE AMAR on 19 May, 2018 - 10:18 am
I have one new Doric if you need it.
Try to contact me.
By sultan khan on 20 May, 2018 - 11:39 am
Hi..
You have not given your particulars or contact details...
>Try to contact me.
Kindly confirm that the DORIC you have is coded for mv input and used for K type thermo couple. Is it a DORIC 400 A type? Kindly give your details to proceed further.
By Amar DAMENE on 22 May, 2018 - 8:33 am
Hi..Khan,
Sorry, Would you contact me by email or viber
dameneamar@gmail.com
viber: +213771887630
Waiting you
By sultan khan on 19 May, 2018 - 12:01 pm
Hi, Mr.David. No one knows about Order code but requirement was for use with K type TC and input being 0 to 25 mv.
Mr. David, does the meter stamped with this order code. OR stamped on base card. Where can we get the details on version or code? Please advice.Thanks.
See the Doric 400 user's manual here:
http://www.advindsys.com/Manuals.htm
The 400 appears to use sensor specific hardware, as shown on page 2-5, an LSI chip and programming module.
Every industrial device I ever seen has a model with configuration and options codes. How Doric accomplished that, I don't know, but you need to some research if you're trying to resurrect this oldie.
FYI, there are lots of 1/8 DIN thermocouple input panel meters, so trade off you time, lost opportunity and what-not against just buying something new that works out-of-the-box.
By sultan khan on 22 May, 2018 - 11:06 am
Hi MR. David,
Thanks a lot for sending me the DORIC manual for reference. There are only two items that can be changed from one to another.
1.LSI chip
2. analogue input module.
The one which was fitted and working was a DORIC for use with K type
TC with mv applied on the V+ and V- terminals. Now the meter is flickering and no response when mv signal applied on the input terminals. Tried to adjust zero (with 0mv)-span adjustment screw and
stability screws etc.. I would like to have practical approach to this problem. If you had come across this problem and sorted out the issue. then Please share your approach to this issue.
Thanks a lot again for your kind response.